1. Soil Nailing Wall
Technical Specifications:
-
Nail Length: 0.5–1.2 times excavation depth
-
Spacing: 1–2 m
-
Inclination Angle: 5°–20° from horizontal
-
Reinforcement: HRB335 or HRB400 steel bars (Ø16–32 mm)
-
Drill Hole Diameter: 70–120 mm
-
Grout Strength: ≥ M10
-
Shotcrete Face: ≥ C20 concrete, ≥ 20 mm rebar cover
Construction Sequence:
-
Slope trimming → 2. Drilling → 3. Nail installation → 4. Grouting → 5. Mesh & reinforcement binding → 6. Shotcrete application
Key Requirements:
-
Groundwater must be controlled before construction
-
Shotcrete machine range: ≥100m horizontal, ≥30m vertical
-
Air compressor: ≥9 m³/min flow rate, >0.5 MPa pressure
-
Delivery hose pressure rating: ≥0.8 MPa
2. Bored Piles
Technical Specifications:
-
Cantilever Piles: Minimum Ø600 mm
-
Capping Beam: Width ≥ pile diameter, height ≥400 mm (≥C20 concrete)
-
Vertical Tolerance: ≤0.5% deviation
-
Positioning Tolerance: ≤50 mm
Construction Sequence:
-
Drilling → 2. Rebar cage installation → 3. Concrete pouring → 4. Capping beam construction
Reinforcement Details:
-
Stiffening hoops: Welded to main bars
-
Spiral ties: Wire-tied to main bars
3. Tieback Anchors
Applications:
-
Combined with soldier piles or soil nailing systems
Construction Sequence:
-
Drilling → 2. Tendon installation → 3. Grouting → 4. Curing → 5. Anchorage assembly → 6. Stressing
Quality Controls:
-
Position Tolerance: ≤100 mm
-
Inclination Tolerance: ≤3%
-
Grout Strength: ≥15 MPa (75% design strength before stressing)
Load Transfer:
Anchors connect to piles via steel wale beams for force distribution.
4. Internal Bracing Systems
Structural Options:
-
Steel Bracing:
-
Connections: Welded or high-strength bolted
-
Wale beam joints: Within 1/3 of the span from supports
-
Pile interface: ≥C20 fine concrete infill
-
Stiffener plates are required at connection nodes
-
-
Concrete Bracing:
-
Minimum concrete grade: C20
-
Monolithic casting within each plane
-
Rigid corner connections
-
Critical Notes:
-
Install load-transfer elements before bracing removal
-
Custom engineering is required for geometry, sections, and connections
5. Earthwork Excavation
Planning Requirements:
-
Excavation Drawings must show:
-
Cut/fill lines, footing locations, elevation markers
-
Deep excavation zones with upper/lower level indicators
-
-
Phased Excavation (Soil Nailing Applications):
-
Example: 2 major phases + 6 sub-phases
-
Initial: 3 sub-phase cuts → Central bulk excavation
-
Followed by bottom-up excavation (300 mm soil left for manual trimming)
-
Winter Work Precautions:
-
Prevent subgrade freezing using loose soil or insulating covers
Waterproofing Systems
1. Concrete Waterproofing (Basement Slab & Walls)
Material Specifications:
-
Cement: ≥32.5 MPa
-
Aggregates:
-
Sand: Medium grade, ≤3% silt, ≤1% clay lumps (non-alkali reactive)
-
Gravel: 5–40 mm, ≤1% silt, ≤0.5% clay lumps
-
Admixtures:
-
Fly ash (≥Grade II, ≤20% content)
-
Silica fume (dosage by testing)
-
Permitted additives: Water reducers, expansion agents, crystalline materials
Waterproofing Methods:
A. Membrane Waterproofing
-
Base Slab: Empty-spread or spot-bonded application
-
Walls: Full-bonded application
-
Lap Joints: ≥10 mm overlap, staggered seams (1/3–1/2 width offset)
-
Corners: 500 mm reinforcement layer, 45°/135° fillets
B. Crystalline Coating
-
Pre-wet surfaces 15 minutes before application
-
Application: 50°–60° trowel angle, 0.8 mm total thickness
-
Cure: Immediate water spray after initial set
C. Polyurethane Coating
-
Weak Points: Additional layer at joints/pipes
-
Thickness: 1.2–2.0 mm (2 coats)
-
Masonry Tie-ins: Remove 2 brick courses for lap joints
2. Post-Construction Joint Waterproofing
-
Install the interior membrane protection layer first
-
Waterstop steel plates centered in the wall thickness
3. Exterior Waterproofing at Grade
-
Termination Point: 150 mm above finish grade
-
Sealing: Metal flashing + sealant (200 mm nail spacing)
-
Expansion Joint: 30 mm gap filled with elastic sealant
This technical guide complies with industry standards for foundation support systems and waterproofing best practices. Proper implementation ensures structural integrity and long-term water resistance.